EMF reading of 30milliGauss close to gas water heater - right above kitchen sink

classic Classic list List threaded Threaded
25 messages Options
12
Reply | Threaded
Open this post in threaded view
|

EMF reading of 30milliGauss close to gas water heater - right above kitchen sink

gariki
Hello all

new member here; i have a kitchen sink right below two gas water heaters that are showing a 30-40milliGauss reading close to it. So at best i am going to be exposed to 20-25milligauss for atleast a couple hours a day doing dishes getting water etc.

In addition power for the home is also located right next to the washers that are showing similarly high reading (which are also located right next to the gas heater); and all of them are located right near the home entrance - so its not like i can avoid them all together.

Given that i think i (and my family members) will be exposed to 30millGauss for about 2-3hours a day. I am just researching about EMF stuff; but from what i can tell this sounds horrible. am i correct?

Other than this part; the rest of the house is our dream house. We are debating whether to stay here (which is hard wood flooring) or move to a carpeted house and deal with the problem that come with carpeting.

In addition: this house is right next to a road that leads to a highway a mile down; so i have a continuous stream of cars going through me; crap..

what would you do? stay or move?

thanks
-gariki

Reply | Threaded
Open this post in threaded view
|

Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink

KathyB
Hi Gariki,

I can't advise on the meter readings.  Look up how close you are to cell towers & antennas on antennasearch.com   How close you are to those is biggest answer.

Electrical issues can be fixed. Living close to a highway is hard with the noise and pollution.  Most antennas are located along highways & major roads. Hardwood floors are healthier than carpet.


Kathy


From: gariki <[hidden email]>
t: [eSens] EMF reading of 30milliGauss close to gas water heater - right above kitchen sink















 
 



 


   
     
     
      Hello all



new member here; i have a kitchen sink right below two gas water heaters that are showing a 30-40milliGauss reading close to it. So at best i am going to be exposed to 20-25milligauss for atleast a couple hours a day doing dishes getting water etc.



In addition power for the home is also located right next to the washers that are showing similarly high reading (which are also located right next to the gas heater); and all of them are located right near the home entrance - so its not like i can avoid them all together.



Given that i think i (and my family members) will be exposed to 30millGauss for about 2-3hours a day. I am just researching about EMF stuff; but from what i can tell this sounds horrible. am i correct?



Other than this part; the rest of the house is our dream house. We are debating whether to stay here (which is hard wood flooring) or move to a carpeted house and deal with the problem that come with carpeting.



In addition: this house is right next to a road that leads to a highway a mile down; so i have a continuous stream of cars going through me; crap..



what would you do? stay or move?



thanks

-gariki





   
     

   
   


 



 










[Non-text portions of this message have been removed]

Reply | Threaded
Open this post in threaded view
|

Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink

gariki
In reply to this post by gariki
any opinions anybody? its kind of urgent for us to decide because of lease signing etc.


--- In [hidden email], "gariki" <chetan.gariki@...> wrote:

>
> Hello all
>
> new member here; i have a kitchen sink right below two gas water heaters that are showing a 30-40milliGauss reading close to it. So at best i am going to be exposed to 20-25milligauss for atleast a couple hours a day doing dishes getting water etc.
>
> In addition power for the home is also located right next to the washers that are showing similarly high reading (which are also located right next to the gas heater); and all of them are located right near the home entrance - so its not like i can avoid them all together.
>
> Given that i think i (and my family members) will be exposed to 30millGauss for about 2-3hours a day. I am just researching about EMF stuff; but from what i can tell this sounds horrible. am i correct?
>
> Other than this part; the rest of the house is our dream house. We are debating whether to stay here (which is hard wood flooring) or move to a carpeted house and deal with the problem that come with carpeting.
>
> In addition: this house is right next to a road that leads to a highway a mile down; so i have a continuous stream of cars going through me; crap..
>
> what would you do? stay or move?
>
> thanks
> -gariki
>


Reply | Threaded
Open this post in threaded view
|

Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink

gariki
In reply to this post by KathyB
Thanks Kathy. Thats a cool site.

But i am specifically concerned about the EMF from my hot water generators and the power source (switch board). Just now learned that my steam cleaner that i would have to use on the carpet shows a reading well above 50 as well (maybe even in the hundreds). I guess there is no place to escape.



--- In [hidden email], KathyB <calicocat477@...> wrote:

>
> Hi Gariki,
>
> I can't advise on the meter readings.  Look up how close you are to cell towers & antennas on antennasearch.com   How close you are to those is biggest answer.
>
> Electrical issues can be fixed. Living close to a highway is hard with the noise and pollution.  Most antennas are located along highways & major roads. Hardwood floors are healthier than carpet.
>
>
> Kathy
>
>
> From: gariki <chetan.gariki@...>
> t: [eSens] EMF reading of 30milliGauss close to gas water heater - right above kitchen sink
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>  
>  
>
>
>
>  
>
>
>    
>      
>      
>       Hello all
>
>
>
> new member here; i have a kitchen sink right below two gas water heaters that are showing a 30-40milliGauss reading close to it. So at best i am going to be exposed to 20-25milligauss for atleast a couple hours a day doing dishes getting water etc.
>
>
>
> In addition power for the home is also located right next to the washers that are showing similarly high reading (which are also located right next to the gas heater); and all of them are located right near the home entrance - so its not like i can avoid them all together.
>
>
>
> Given that i think i (and my family members) will be exposed to 30millGauss for about 2-3hours a day. I am just researching about EMF stuff; but from what i can tell this sounds horrible. am i correct?
>
>
>
> Other than this part; the rest of the house is our dream house. We are debating whether to stay here (which is hard wood flooring) or move to a carpeted house and deal with the problem that come with carpeting.
>
>
>
> In addition: this house is right next to a road that leads to a highway a mile down; so i have a continuous stream of cars going through me; crap..
>
>
>
> what would you do? stay or move?
>
>
>
> thanks
>
> -gariki
>
>
>
>
>
>    
>      
>
>    
>    
>
>
>  
>
>
>
>  
>
>
>
>
>
>
>
>
>
>
> [Non-text portions of this message have been removed]
>


Reply | Threaded
Open this post in threaded view
|

Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink

Marc Martin
Administrator
On 10/2/2011 9:11 AM, gariki wrote:
> Thanks Kathy. Thats a cool site.
>
>But i am specifically concerned about the EMF from my hot water generators
>and the power source (switch board). Just now learned that my steam
cleaner
>that i would have to use on the carpet shows a reading well above 50
as well
>(maybe even in the hundreds). I guess there is no place to escape.

Well, you may be focused on the wrong thing -- the milligauss reading
doesn't seem to be the primary problem when it comes to health
problems.  Rather it is the high-frequency noise that may or may not
be present, and your meter isn't even trying to detect.

Marc
Reply | Threaded
Open this post in threaded view
|

Re:Magnetite And Cryptochromes and ES?

Christina Steils
In reply to this post by gariki
Do we have to much in our bodies?

electric-fields.bris.ac.uk

[Non-text portions of this message have been removed]

Reply | Threaded
Open this post in threaded view
|

Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink

gariki
In reply to this post by Marc Martin
high frequency noise? something i never thought about in particular. Can you point me to more info or tell me more about it.

thanks!


--- In [hidden email], Marc Martin <marc@...> wrote:

>
> On 10/2/2011 9:11 AM, gariki wrote:
> > Thanks Kathy. Thats a cool site.
> >
> >But i am specifically concerned about the EMF from my hot water generators
> >and the power source (switch board). Just now learned that my steam
> cleaner
> >that i would have to use on the carpet shows a reading well above 50
> as well
> >(maybe even in the hundreds). I guess there is no place to escape.
>
> Well, you may be focused on the wrong thing -- the milligauss reading
> doesn't seem to be the primary problem when it comes to health
> problems.  Rather it is the high-frequency noise that may or may not
> be present, and your meter isn't even trying to detect.
>
> Marc
>


Reply | Threaded
Open this post in threaded view
|

Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink

Marc Martin
Administrator
> high frequency noise? something i never thought about in particular.
> Can you point me to more info or tell me more about it.

Hi frequency noise is the stuff in the kilohertz, megahertz, and
gigahertz regimes -- something that a 60hz EMF meter does not
detect.  This stuff comes from a variety of modern electronics --
refrigerators, TVs, computers, florescent lights, wireless
phones, dimmer switches, cellphones, wi-fi, smart meters for
utilities, etc.  -- and if you share the same power transformer
with your neighbors, this stuff could be coming into your
house from next door...

I find that my health problems comes from these higher
frequencies -- for example, I can recall getting terrible
symptoms from a 15" LCD monitor, even though my EMF
meter showed nearly zero milligauss.  However, if I
put an AM radio next to the monitor (550 khz - 1200 khz),
I could hear all sorts of nasty buzzing on the radio.

Marc
Reply | Threaded
Open this post in threaded view
|

Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink

emraware
In reply to this post by gariki
Magnetic fields do matter.  See Bioinitiative Report, Seletun scientific statement 2011, among others.

You need to first identify the source of the magnetic field.

If the source is an appliance, usually 1 meter distance is sufficient.  

If the source is net currents on the wire caused by a wiring error like ganged neutrals, then you'd better correct the wiring error.

If the source is external from the outside power line or water pipes (e.g., still there when all the circuit breakers are off), you may not have many good choices.  

Shielding is not easy and expensive.

You might want to rearrange living spaces to minimize your time in high magnetic field areas.

--- In [hidden email], "gariki" <chetan.gariki@...> wrote:

>
> Thanks Kathy. Thats a cool site.
>
> But i am specifically concerned about the EMF from my hot water generators and the power source (switch board). Just now learned that my steam cleaner that i would have to use on the carpet shows a reading well above 50 as well (maybe even in the hundreds). I guess there is no place to escape.
>
>
>
> --- In [hidden email], KathyB <calicocat477@> wrote:
> >
> > Hi Gariki,
> >
> > I can't advise on the meter readings.  Look up how close you are to cell towers & antennas on antennasearch.com   How close you are to those is biggest answer.
> >
> > Electrical issues can be fixed. Living close to a highway is hard with the noise and pollution.  Most antennas are located along highways & major roads. Hardwood floors are healthier than carpet.
> >
> >
> > Kathy
> >
> >
> > From: gariki <chetan.gariki@>
> > t: [eSens] EMF reading of 30milliGauss close to gas water heater - right above kitchen sink
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >  
> >  
> >
> >
> >
> >  
> >
> >
> >    
> >      
> >      
> >       Hello all
> >
> >
> >
> > new member here; i have a kitchen sink right below two gas water heaters that are showing a 30-40milliGauss reading close to it. So at best i am going to be exposed to 20-25milligauss for atleast a couple hours a day doing dishes getting water etc.
> >
> >
> >
> > In addition power for the home is also located right next to the washers that are showing similarly high reading (which are also located right next to the gas heater); and all of them are located right near the home entrance - so its not like i can avoid them all together.
> >
> >
> >
> > Given that i think i (and my family members) will be exposed to 30millGauss for about 2-3hours a day. I am just researching about EMF stuff; but from what i can tell this sounds horrible. am i correct?
> >
> >
> >
> > Other than this part; the rest of the house is our dream house. We are debating whether to stay here (which is hard wood flooring) or move to a carpeted house and deal with the problem that come with carpeting.
> >
> >
> >
> > In addition: this house is right next to a road that leads to a highway a mile down; so i have a continuous stream of cars going through me; crap..
> >
> >
> >
> > what would you do? stay or move?
> >
> >
> >
> > thanks
> >
> > -gariki
> >
> >
> >
> >
> >
> >    
> >      
> >
> >    
> >    
> >
> >
> >  
> >
> >
> >
> >  
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> > [Non-text portions of this message have been removed]
> >
>


Reply | Threaded
Open this post in threaded view
|

Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink

C.a.b. Johnson
In reply to this post by gariki

--- On Sun, 10/2/11, gariki <[hidden email]> wrote

what would you do? stay or move?

Hi,

If the other house has less problems with traffic, EMF's, cell towers, etc.  then carpet can be easily removed and a floor put down for probably less expense than it would be to deal with the EMF problems. 

For example, you would have to use Mu Metal on the ceiling or floor and the wall to block the EMF's from your area.  But enough sheets to do the job would probably cost you about $2,000 to $5,000, You could put in a floor in the other house for the same amount of money.  Just my 2 cents.

C. Johhnson
Superdrove







     




     

  .


 








 





[Non-text portions of this message have been removed]

Reply | Threaded
Open this post in threaded view
|

Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink

gariki
Thanks for the inputs everyone.

We have decided to move back to the carpeted apartment (actually it was one we lived in for 2years an year ago). The carpet is about 1year old; so neither too new to offgas nor too old to be hosting a bunch of dust and germs etc. Unfortunately this is the middle floor and we cant change it to carpet in the future also.

But because i am more aware now than before we have eliminated both ground floor (because of emfs from smart meters) and top floors due to emfs from wiring above. Actually the ground floor was ok; since emf was only at one spot in the house; the top floors; of both the houses i checked had emf above 6-7 all through the house due to wiring in the crawl space above.

After this experience; we wonder.. where is the world going; by the time my kids are old enough there wont be any place to hide. jeez.


-gariki

--- In [hidden email], "C.a.b. Johnson" <superdrove@...> wrote:

>
>
> --- On Sun, 10/2/11, gariki <chetan.gariki@...> wrote
>
> what would you do? stay or move?
>
> Hi,
>
> If the other house has less problems with traffic, EMF's, cell towers, etc.  then carpet can be easily removed and a floor put down for probably less expense than it would be to deal with the EMF problems. 
>
> For example, you would have to use Mu Metal on the ceiling or floor and the wall to block the EMF's from your area.  But enough sheets to do the job would probably cost you about $2,000 to $5,000, You could put in a floor in the other house for the same amount of money.  Just my 2 cents.
>
> C. Johhnson
> Superdrove
>
>
>
>
>
>
>
>      
>
>
>
>
>      
>
>   .
>
>
>  
>
>
>
>
>
>
>
>
>  
>
>
>
>
>
> [Non-text portions of this message have been removed]
>


Reply | Threaded
Open this post in threaded view
|

Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink

BiBrun
Usually wiring isn't so bad except when there are
loops caused by ground loops or ganged neutrals.
There are a couple books on this (one by Ed Leeper I used).
Unfortunately probably 90% of electricians don't understand the
problem.  Shielded wiring is nice, but won't solve the problem.
I suspect there was a similar "net current" probably at
your water heaters too... often this can be fixed by just
disconnecting the ground wire from the water pipes, though
code usual requires that wire be connected.

On Tue, Oct 4, 2011 at 8:53 AM, gariki <[hidden email]> wrote:

> **
>
>
> Thanks for the inputs everyone.
>
> We have decided to move back to the carpeted apartment (actually it was one
> we lived in for 2years an year ago). The carpet is about 1year old; so
> neither too new to offgas nor too old to be hosting a bunch of dust and
> germs etc. Unfortunately this is the middle floor and we cant change it to
> carpet in the future also.
>
> But because i am more aware now than before we have eliminated both ground
> floor (because of emfs from smart meters) and top floors due to emfs from
> wiring above. Actually the ground floor was ok; since emf was only at one
> spot in the house; the top floors; of both the houses i checked had emf
> above 6-7 all through the house due to wiring in the crawl space above.
>
> After this experience; we wonder.. where is the world going; by the time my
> kids are old enough there wont be any place to hide. jeez.
>
> -gariki
>
> --- In [hidden email], "C.a.b. Johnson" <superdrove@...> wrote:
> >
> >
> > --- On Sun, 10/2/11, gariki <chetan.gariki@...> wrote
>
> >
> > what would you do? stay or move?
> >
> > Hi,
> >
> > If the other house has less problems with traffic, EMF's, cell towers,
> etc.  then carpet can be easily removed and a floor put down for probably
> less expense than it would be to deal with the EMF problems.
> >
> > For example, you would have to use Mu Metal on the ceiling or floor and
> the wall to block the EMF's from your area.  But enough sheets to do the job
> would probably cost you about $2,000 to $5,000, You could put in a floor in
> the other house for the same amount of money.  Just my 2 cents.
> >
> > C. Johhnson
> > Superdrove
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> > .
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> >
> > [Non-text portions of this message have been removed]
> >
>
>  
>


[Non-text portions of this message have been removed]



------------------------------------

Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/eSens/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/eSens/join
    (Yahoo! ID required)

<*> To change settings via email:
    [hidden email]
    [hidden email]

<*> To unsubscribe from this group, send an email to:
    [hidden email]

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/

Reply | Threaded
Open this post in threaded view
|

Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink

Elizabeth thode

According to the National Electrical Code, just updated this past year: it is NO longer code for water pipes to be grounded. Code calls for grounding of water line AT the service entrance (this is where the water comes into the house.)
Lizzie
 

> To: [hidden email]
> From: [hidden email]
> Date: Tue, 4 Oct 2011 10:18:40 -0600
> Subject: Re: [eSens] Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink
>
> Usually wiring isn't so bad except when there are
> loops caused by ground loops or ganged neutrals.
> There are a couple books on this (one by Ed Leeper I used).
> Unfortunately probably 90% of electricians don't understand the
> problem. Shielded wiring is nice, but won't solve the problem.
> I suspect there was a similar "net current" probably at
> your water heaters too... often this can be fixed by just
> disconnecting the ground wire from the water pipes, though
> code usual requires that wire be connected.
>
> On Tue, Oct 4, 2011 at 8:53 AM, gariki <[hidden email]> wrote:
>
> > **
> >
> >
> > Thanks for the inputs everyone.
> >
> > We have decided to move back to the carpeted apartment (actually it was one
> > we lived in for 2years an year ago). The carpet is about 1year old; so
> > neither too new to offgas nor too old to be hosting a bunch of dust and
> > germs etc. Unfortunately this is the middle floor and we cant change it to
> > carpet in the future also.
> >
> > But because i am more aware now than before we have eliminated both ground
> > floor (because of emfs from smart meters) and top floors due to emfs from
> > wiring above. Actually the ground floor was ok; since emf was only at one
> > spot in the house; the top floors; of both the houses i checked had emf
> > above 6-7 all through the house due to wiring in the crawl space above.
> >
> > After this experience; we wonder.. where is the world going; by the time my
> > kids are old enough there wont be any place to hide. jeez.
> >
> > -gariki
> >
> > --- In [hidden email], "C.a.b. Johnson" <superdrove@...> wrote:
> > >
> > >
> > > --- On Sun, 10/2/11, gariki <chetan.gariki@...> wrote
> >
> > >
> > > what would you do? stay or move?
> > >
> > > Hi,
> > >
> > > If the other house has less problems with traffic, EMF's, cell towers,
> > etc. then carpet can be easily removed and a floor put down for probably
> > less expense than it would be to deal with the EMF problems.
> > >
> > > For example, you would have to use Mu Metal on the ceiling or floor and
> > the wall to block the EMF's from your area. But enough sheets to do the job
> > would probably cost you about $2,000 to $5,000, You could put in a floor in
> > the other house for the same amount of money. Just my 2 cents.
> > >
> > > C. Johhnson
> > > Superdrove
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > > .
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > > [Non-text portions of this message have been removed]
> > >
> >
> >
> >
>
>
> [Non-text portions of this message have been removed]
>
>
>
> ------------------------------------
>
> Yahoo! Groups Links
>
>
>
     

[Non-text portions of this message have been removed]

Reply | Threaded
Open this post in threaded view
|

Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink

charles-4
No, it is the other way around.

They do not want to ground the water pipes.
They want want to use the water pipes for grounding.

Greetings,
Charles Claessens
member Verband Baubiologie
www.milieuziektes.nl
www.milieuziektes.be
www.hetbitje.nl
checked by Norton


  ----- Original Message -----
  From: Elizabeth thode
  To: [hidden email]
  Sent: Tuesday, October 04, 2011 6:59 PM
  Subject: RE: [eSens] Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink



  According to the National Electrical Code, just updated this past year: it is NO longer code for water pipes to be grounded. Code calls for grounding of water line AT the service entrance (this is where the water comes into the house.)
  Lizzie
   



[Non-text portions of this message have been removed]

Reply | Threaded
Open this post in threaded view
|

Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink

Elizabeth thode

Yes, you are correct. And for years/decades, in the US, it was Code to do it that way.
It is now no longer Code to use the water pipes for grounding.
Lizzie
 



To: [hidden email]
From: [hidden email]
Date: Tue, 4 Oct 2011 19:23:17 +0200
Subject: Re: [eSens] Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink


 



No, it is the other way around.

They do not want to ground the water pipes.
They want want to use the water pipes for grounding.

Greetings,
Charles Claessens
member Verband Baubiologie
www.milieuziektes.nl
www.milieuziektes.be
www.hetbitje.nl
checked by Norton

----- Original Message -----
From: Elizabeth thode
To: [hidden email]
Sent: Tuesday, October 04, 2011 6:59 PM
Subject: RE: [eSens] Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink

According to the National Electrical Code, just updated this past year: it is NO longer code for water pipes to be grounded. Code calls for grounding of water line AT the service entrance (this is where the water comes into the house.)
Lizzie


[Non-text portions of this message have been removed]




     

[Non-text portions of this message have been removed]

Reply | Threaded
Open this post in threaded view
|

Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink

evie15422
In reply to this post by BiBrun
Hi Bill and Gariki,

<Unfortunately probably 90% of electricians don't understand the
problem.>

So true.  I could have gone to school and learned wiring myself and rewired our house, also, in the time it took to find one who would do it the way I asked!  It was a painful process.

<Shielded wiring is nice, but won't solve the problem.>

We had shielded wiring put in, however, that only works as well as your ability to keep frequencies out of the house.  In some circumstances emfs penetrate our brick walls.  We have particular problems with emfs penetrating during a 3 hour window on Sunday mornings.  When this happens, those frequencies radiate around the house due to the metal shielded wiring itself.  So, I would definitely not put metal wiring in in the future, seeing smart meters and possible satellite transmissions coming down the pike.


<I suspect there was a similar "net current" probably at
your water heaters too... >


Gariki, I don't remember all the particulars of your original post, however, I remember you writing about having problems around your sink....  We had similar problems with our water and water heater....  To fix it we bought a gas only hot water heater and had it installed, and we had the water pipes moved to a different course into the house which avoided electric wiring.  (In our circumstance, the water pipes snaked all thru the house and under the bedrooms, when all they needed to do was to come in to the back of the house and go directly to the bath and kitchen.)  I don't know whether this is helpful info for you or not, but if you are trading a single dwelling for an apartment or condo, I would definitely keep the single dwelling and change the water situation.  If/ when smart meters come to your area, you will need all the space from others' meters that you can get. 


My 2 cents,
Diane 


________________________________

[Non-text portions of this message have been removed]

Reply | Threaded
Open this post in threaded view
|

Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink

evie15422
In reply to this post by Elizabeth thode
I believe, tho, Lizzie, there are State codes which enforce this.  Here in Pa, they want water pipes grounded, but I know for fact this is not the case in all States.


Diane



________________________________
From: Elizabeth thode <[hidden email]>
To: [hidden email]
Sent: Tuesday, October 4, 2011 12:59 PM
Subject: RE: [eSens] Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink


 

According to the National Electrical Code, just updated this past year: it is NO longer code for water pipes to be grounded. Code calls for grounding of water line AT the service entrance (this is where the water comes into the house.)
Lizzie


> To: [hidden email]
> From: [hidden email]
> Date: Tue, 4 Oct 2011 10:18:40 -0600
> Subject: Re: [eSens] Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink
>
> Usually wiring isn't so bad except when there are
> loops caused by ground loops or ganged neutrals.
> There are a couple books on this (one by Ed Leeper I used).
> Unfortunately probably 90% of electricians don't understand the
> problem. Shielded wiring is nice, but won't solve the problem.
> I suspect there was a similar "net current" probably at
> your water heaters too... often this can be fixed by just
> disconnecting the ground wire from the water pipes, though
> code usual requires that wire be connected.
>
> On Tue, Oct 4, 2011 at 8:53 AM, gariki <[hidden email]> wrote:
>
> > **
> >
> >
> > Thanks for the inputs everyone.
> >
> > We have decided to move back to the carpeted apartment (actually it was one
> > we lived in for 2years an year ago). The carpet is about 1year old; so
> > neither too new to offgas nor too old to be hosting a bunch of dust and
> > germs etc. Unfortunately this is the middle floor and we cant change it to
> > carpet in the future also.
> >
> > But because i am more aware now than before we have eliminated both ground
> > floor (because of emfs from smart meters) and top floors due to emfs from
> > wiring above. Actually the ground floor was ok; since emf was only at one
> > spot in the house; the top floors; of both the houses i checked had emf
> > above 6-7 all through the house due to wiring in the crawl space above.
> >
> > After this experience; we wonder.. where is the world going; by the time my
> > kids are old enough there wont be any place to hide. jeez.
> >
> > -gariki
> >
> > --- In [hidden email], "C.a.b. Johnson" <superdrove@...> wrote:
> > >
> > >
> > > --- On Sun, 10/2/11, gariki <chetan.gariki@...> wrote
> >
> > >
> > > what would you do? stay or move?
> > >
> > > Hi,
> > >
> > > If the other house has less problems with traffic, EMF's, cell towers,
> > etc. then carpet can be easily removed and a floor put down for probably
> > less expense than it would be to deal with the EMF problems.
> > >
> > > For example, you would have to use Mu Metal on the ceiling or floor and
> > the wall to block the EMF's from your area. But enough sheets to do the job
> > would probably cost you about $2,000 to $5,000, You could put in a floor in
> > the other house for the same amount of money. Just my 2 cents.
> > >
> > > C. Johhnson
> > > Superdrove
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > > .
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > > [Non-text portions of this message have been removed]
> > >
> >
> >
> >
>
>
> [Non-text portions of this message have been removed]
>
>
>
> ------------------------------------
>
> Yahoo! Groups Links
>
>
>


[Non-text portions of this message have been removed]


 

[Non-text portions of this message have been removed]

Reply | Threaded
Open this post in threaded view
|

Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink

gariki
In reply to this post by evie15422
Hello Diane,

Thanks for your post. Yes; our kitchen sink where we do most dishes is right below the heaters. And i talked to the landlord about moving the sink elsewhere but he said it would need ripping a lot of stuff. Anyways because of this and other things we are moving out; back into the apartment i was an year ago.

For the most part this place is clean. Now i hear a lot of concern from folks on this board about smart meters; before i joined this board a couple days ago; i never even gave them a single thought. Now for the apartmets i am moving to; there are a set of about 6 meters attached to the wall right outside on the ground (first) floor. So in the first floor bedroom there is some of that signal (i was using a cheap emf meter; but it picked up about 7-9 milligauss inside there). On the second floor that must be significantly lower but now that i am aware of this atleast i will not put my bed near that wall for sure.

BTW how bad are these smart meters? would appreciate any links.

thanks!
-gariki

--- In [hidden email], Evie <evie15422@...> wrote:

>
> Hi Bill and Gariki,
>
> <Unfortunately probably 90% of electricians don't understand the
> problem.>
>
> So true.  I could have gone to school and learned wiring myself and rewired our house, also, in the time it took to find one who would do it the way I asked!  It was a painful process.
>
> <Shielded wiring is nice, but won't solve the problem.>
>
> We had shielded wiring put in, however, that only works as well as your ability to keep frequencies out of the house.  In some circumstances emfs penetrate our brick walls.  We have particular problems with emfs penetrating during a 3 hour window on Sunday mornings.  When this happens, those frequencies radiate around the house due to the metal shielded wiring itself.  So, I would definitely not put metal wiring in in the future, seeing smart meters and possible satellite transmissions coming down the pike.
>
>
> <I suspect there was a similar "net current" probably at
> your water heaters too... >
>
>
> Gariki, I don't remember all the particulars of your original post, however, I remember you writing about having problems around your sink....  We had similar problems with our water and water heater....  To fix it we bought a gas only hot water heater and had it installed, and we had the water pipes moved to a different course into the house which avoided electric wiring.  (In our circumstance, the water pipes snaked all thru the house and under the bedrooms, when all they needed to do was to come in to the back of the house and go directly to the bath and kitchen.)  I don't know whether this is helpful info for you or not, but if you are trading a single dwelling for an apartment or condo, I would definitely keep the single dwelling and change the water situation.  If/ when smart meters come to your area, you will need all the space from others' meters that you can get. 
>
>
> My 2 cents,
> Diane 
>
>
> ________________________________
>
> [Non-text portions of this message have been removed]
>


Reply | Threaded
Open this post in threaded view
|

Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink

KathyB
In reply to this post by evie15422

I was told new construction grounds them to a grounding rod & not on water pipes as used to be done.

Kathy

From: Evie <[hidden email]>
Subject: Re: [eSens] Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink
To: "[hidden email]" <[hidden email]>
Date: Wednesday, October 5, 2011, 12:29 PM















 
 



 


   
     
     
      I believe, tho, Lizzie, there are State codes which enforce this.  Here in Pa, they want water pipes grounded, but I know for fact this is not the case in all States.



Diane



________________________________

From: Elizabeth thode <[hidden email]>

To: [hidden email]

Sent: Tuesday, October 4, 2011 12:59 PM

Subject: RE: [eSens] Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink



 



According to the National Electrical Code, just updated this past year: it is NO longer code for water pipes to be grounded. Code calls for grounding of water line AT the service entrance (this is where the water comes into the house.)

Lizzie



> To: [hidden email]

> From: [hidden email]

> Date: Tue, 4 Oct 2011 10:18:40 -0600

> Subject: Re: [eSens] Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink

>

> Usually wiring isn't so bad except when there are

> loops caused by ground loops or ganged neutrals.

> There are a couple books on this (one by Ed Leeper I used).

> Unfortunately probably 90% of electricians don't understand the

> problem. Shielded wiring is nice, but won't solve the problem.

> I suspect there was a similar "net current" probably at

> your water heaters too... often this can be fixed by just

> disconnecting the ground wire from the water pipes, though

> code usual requires that wire be connected.

>



[Non-text portions of this message have been removed]

Reply | Threaded
Open this post in threaded view
|

Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink

evie15422
In reply to this post by gariki
Oh sorry, Gariki,

I thought you owned the house.  Yes, changing things will not work for you.  :(


I have to go now or I would look for you, but Loni and Emraware and Andrew McAfee are 3 names you could try for info on Smart meters.  Plug these names into the anchives search with the words "smart meters".

Good luck,
Diane



________________________________
From: gariki <[hidden email]>
To: [hidden email]
Sent: Wednesday, October 5, 2011 1:39 PM
Subject: [eSens] Re: EMF reading of 30milliGauss close to gas water heater - right above kitchen sink


 
Hello Diane,

Thanks for your post. Yes; our kitchen sink where we do most dishes is right below the heaters. And i talked to the landlord about moving the sink elsewhere but he said it would need ripping a lot of stuff. Anyways because of this and other things we are moving out; back into the apartment i was an year ago.

For the most part this place is clean. Now i hear a lot of concern from folks on this board about smart meters; before i joined this board a couple days ago; i never even gave them a single thought. Now for the apartmets i am moving to; there are a set of about 6 meters attached to the wall right outside on the ground (first) floor. So in the first floor bedroom there is some of that signal (i was using a cheap emf meter; but it picked up about 7-9 milligauss inside there). On the second floor that must be significantly lower but now that i am aware of this atleast i will not put my bed near that wall for sure.

BTW how bad are these smart meters? would appreciate any links.

thanks!
-gariki

--- In [hidden email], Evie <evie15422@...> wrote:

>
> Hi Bill and Gariki,
>
> <Unfortunately probably 90% of electricians don't understand the
> problem.>
>
> So true.  I could have gone to school and learned wiring myself and rewired our house, also, in the time it took to find one who would do it the way I asked!  It was a painful process.
>
> <Shielded wiring is nice, but won't solve the problem.>
>
> We had shielded wiring put in, however, that only works as well as your ability to keep frequencies out of the house.  In some circumstances emfs penetrate our brick walls.  We have particular problems with emfs penetrating during a 3 hour window on Sunday mornings.  When this happens, those frequencies radiate around the house due to the metal shielded wiring itself.  So, I would definitely not put metal wiring in in the future, seeing smart meters and possible satellite transmissions coming down the pike.
>
>
> <I suspect there was a similar "net current" probably at
> your water heaters too... >
>
>
> Gariki, I don't remember all the particulars of your original post, however, I remember you writing about having problems around your sink....  We had similar problems with our water and water heater....  To fix it we bought a gas only hot water heater and had it installed, and we had the water pipes moved to a different course into the house which avoided electric wiring.  (In our circumstance, the water pipes snaked all thru the house and under the bedrooms, when all they needed to do was to come in to the back of the house and go directly to the bath and kitchen.)  I don't know whether this is helpful info for you or not, but if you are trading a single dwelling for an apartment or condo, I would definitely keep the single dwelling and change the water situation.  If/ when smart meters come to your area, you will need all the space from others' meters that you can get. 
>
>
> My 2 cents,
> Diane 
>
>
> ________________________________
>
> [Non-text portions of this message have been removed]
>


 

[Non-text portions of this message have been removed]